My AC guy was on my boat yesterday and in the context of back flushing the raw water lines found that the antique start/run knob switch on the salon unit 3 knob control was toast. Replaced that. Related wiring harness can stand replacement, this will happen next week.
My electrical guy was on the boat today. He tested amp draw on the AC units at the condensers individually, then at the shore inlet with both units running full blast. Total draw - condensers, air handlers and pump is 23 amps. Voltage holds and 110v. with all running. He states "you're good".
Both AC units are working perfectly and pumping out plenty of cold air. He further states "run them til they break!"
When they do break, there are some very good options for modern replacements.
We are going to install digital volt/amp meters for both 30 amp panels so I can see whats happening at a glance. This per Pascal's very sound suggestion.
So, for now I am back up and running.
Eric~
Not knowing your system sizes...23 amps seems a bit low to me for two 115 volt systems...Well...As I say...Depending on system size...
The way we always figured it for installations, was the amp draw for the systems pretty closely matches the system BTU...
For instance we would figure a 16K system at 16 amps average...The condensing unit was rated at 12 amps cool & 15 amps in heat...Then add the blower & pump to that total...blower maybe as much as 3 amps for a EBS-16 (which was common on Hatt's) & pump as much as 5 amps (if a single large pump for multiple systems)
Blower & pump average stay pretty much the same...But condensing unit (compressor) amperage can change quite a bit with water & cabin temps & the condition of the water system & condenser coil...
That 16K condensing unit in 90 degree seawater & a 100 degree cabin with a dirty scaled up condenser coil might draw as much as 18-19 amps by itself...This is why I mentioned ACID flush earlier...Not just a back flush...A simple back flush will not remove scale from that seawater condenser that may be preventing good heat transfer to the water...
Normal system head pressure under those conditions should be between say 260 to maybe 300 psi....Pressure rises with heat...So if water flow is reduced, or the condenser is scaled up (which makes it hotter)...Then that pressure is much higher...Yes the system will continue to run because the high pressure switch does not cut it off until 425 psi...But as you see, you have quite a way to go between normal & cut out (at least 125 psi)...The compressor pumping against that higher pressure is working much harder & therefore drawing much more than normal amperage.
This method of sizing usually produced spot on predictions for overall amp draw of older 115 volt split systems, with just a bit of fudge factor....The newer systems negate this method somewhat because they are more efficient...
So going by my old method...A 16K & a 12K 115 volt system is about 28 amps average...The comfortable (close) limit of a 30 amp service...Yes there are dual 16K systems on 30 amp cords/services but they must be squeaky clean in warmer climates & they do have the most cord/receptacle troubles...