Good afternoon all;
My hvac circuit (50amp, 125volt. not 240v) has begun consuming 40amps instead of the usual 22amps. also the main and individual breakers get hot, not warm. The panel ammeter reads 20 amps with either hvac on and 40 amps with both on.
The hvac master breaker feeds two 20 amp breakers and each breaker has one 12btu self contained unit.
I have changed out the starboard inlet receptacle, swapped power cords, switched over to the port inlet, changed out the port inlet, changed the individual hvac breakers, changed out the 50amp master breaker. still - each hvac unt pulls 20 amps. I know it's not the hvac units themselves as I have disconnected each one while the other was connected and still the ammeter shows 20amps. Crazy because a clamp ammeter tester on each hvac cable shows about 11amps being consumed by the individual units. also, at the shore power pedestal, shows 11amps consumed by each unit and about 22amps when both are turned on. I'm now thinking maybe the cables running from the inlets to the circuit breaker is bad somewhere. the port and starboard inlets must be joined in a junction somewhere because each inlet has one cable and the breaker box only has one cable entering it.
yes, voltage tested everywhere and about 117 volts beginning at pedestal and ending at each hvac circuit.
Any ideas and any idea where the two inlets could be junctioned?
1965 50' hatteras motoryacht.
Thanks for any and all ideas and suggestions.
My hvac circuit (50amp, 125volt. not 240v) has begun consuming 40amps instead of the usual 22amps. also the main and individual breakers get hot, not warm. The panel ammeter reads 20 amps with either hvac on and 40 amps with both on.
The hvac master breaker feeds two 20 amp breakers and each breaker has one 12btu self contained unit.
I have changed out the starboard inlet receptacle, swapped power cords, switched over to the port inlet, changed out the port inlet, changed the individual hvac breakers, changed out the 50amp master breaker. still - each hvac unt pulls 20 amps. I know it's not the hvac units themselves as I have disconnected each one while the other was connected and still the ammeter shows 20amps. Crazy because a clamp ammeter tester on each hvac cable shows about 11amps being consumed by the individual units. also, at the shore power pedestal, shows 11amps consumed by each unit and about 22amps when both are turned on. I'm now thinking maybe the cables running from the inlets to the circuit breaker is bad somewhere. the port and starboard inlets must be joined in a junction somewhere because each inlet has one cable and the breaker box only has one cable entering it.
yes, voltage tested everywhere and about 117 volts beginning at pedestal and ending at each hvac circuit.
Any ideas and any idea where the two inlets could be junctioned?
1965 50' hatteras motoryacht.
Thanks for any and all ideas and suggestions.