On our last trip, a recurring issue with our generator became annoying enough that we actually started studying it and experimenting.
Background:
Occasionally, which over time has become more frequently, our newer AC blowers and new galley appliances would begin to act up. In the past, we would change the small filter on the genset (Westerbeke 15k) and all would be well for awhile.
After we put a 2micron filter in the Racor, and replaced the 7 micron on the genset, within an hour we were back where we started. Our first experiment was to shut down the genset for 20 minutes and restart without changing any filters (which always looked clean). It worked for a while, which started me looking at other things. Voltage was stable, so we started monitoring frequency. With a small to moderate load, it's putting out up to 64 hz, which is when things go wonky.
Studying the manual, I noticed that the spec for full load hz was a bit lower than no load, so the next experiment was to fire up all of the ac units, setting the thermostats so that they could not possibly "satisfy". Everything ran find for two days, and we slept well under blankets.
The simple answer is to adjust the governor to get the hz back in spec, which I plan to do, but the whole exercise of getting here raised some questions in my mind, if anyone has some wisdom (no lack of that here, right?) they might be willing to share.
First, the genset apparently does not run through the isolation transformers, which seems common. Why is this? Would the transformers not correct the voltage and frequency as they do with shore power?
Second, there is an optional voltage regulator mentioned in the Westerbeke documentation. It does not mention frequency regulation, but I'm wondering if this is a worthwhile addition to the unit.
I've read through the procedures for adjusting the governor, but would appreciate any real life experience tips on doing so.
Thanks,
Background:
Occasionally, which over time has become more frequently, our newer AC blowers and new galley appliances would begin to act up. In the past, we would change the small filter on the genset (Westerbeke 15k) and all would be well for awhile.
After we put a 2micron filter in the Racor, and replaced the 7 micron on the genset, within an hour we were back where we started. Our first experiment was to shut down the genset for 20 minutes and restart without changing any filters (which always looked clean). It worked for a while, which started me looking at other things. Voltage was stable, so we started monitoring frequency. With a small to moderate load, it's putting out up to 64 hz, which is when things go wonky.
Studying the manual, I noticed that the spec for full load hz was a bit lower than no load, so the next experiment was to fire up all of the ac units, setting the thermostats so that they could not possibly "satisfy". Everything ran find for two days, and we slept well under blankets.
The simple answer is to adjust the governor to get the hz back in spec, which I plan to do, but the whole exercise of getting here raised some questions in my mind, if anyone has some wisdom (no lack of that here, right?) they might be willing to share.
First, the genset apparently does not run through the isolation transformers, which seems common. Why is this? Would the transformers not correct the voltage and frequency as they do with shore power?
Second, there is an optional voltage regulator mentioned in the Westerbeke documentation. It does not mention frequency regulation, but I'm wondering if this is a worthwhile addition to the unit.
I've read through the procedures for adjusting the governor, but would appreciate any real life experience tips on doing so.
Thanks,