TedZ said:
I'm aware that the GFI's protect downstream. To think otherwise would be nonesense.
Hatteras and others go through the trouble to bond everything in the boat and to continue that bonding to the shore power. Most of us operate in that mode.
Hatteras and others do this
on boats that have no isolation transformer because it is NECESSARY in that configuration, especially if there are no GFIs involved.
For some reason when using isolation transformers you advise abandoning that philosophy when it is unnecessary and can be dangerous. It is simply based in a misunderstanding the role of the modern isolation transformer.
Nonsense.
It is no more "dangerous" than it is to run a GENSET on board.
A Generator is a power source. So is an isolation transformer.
Do the following:
1. Take EITHER a genset OR an isolation transformer secondary.
2. DO NOT connect any pole of the output to ground (you have three bare wires sticking out - black, white and green - assuming 120V output)
3. Sitting on your boat, immerse ANY of the three wires in the water (not more than one however!)
NOTHING HAPPENS. No current flows. NONE! Not even if you stick the HOT wire in the water! Not even if you GRAB the hot wire and stick your FOOT in the water. (BTW, I explicitly recommend against grabbing the wire, because if there is a connection between neutral and ground that you don't know about - like a 220V dryer that is wired the "old way" - you will DIE!)
Why not? Because there is no return current path. There is nowhere for the energy to go! For current to flow there must be a COMPLETE CIRCUIT. The transformer (or genset) prevents that circuit from existing, as there is an "open" in the middle.
Now, connect your GREEN wire (from either the genset or the isolation transformer outlet) to the shoreside GREEN wire. NOW immerse the hot. You get a HUGE current flow through the water, back to your submerged underwater metals, and back to shore. This is a fault condition. If you're lucky you trip a breaker. If not you fry things - including those metals. If YOU come between that hot and water, YOU FRY.
So why do people make noise about the difference between an "isolation" and "polarization" transformer? Because it is possible for the TRANSFORMER ITSELF to have a fault in it - specifically, there can be a short in the windings between the primary and secondary side. An isolation transformer has a shield between those windings that can take the entire fault current and dump it back to the primary side's ground without melting. The design parameters necessary to do this are complex because doing so tends to interfere with the magnetic flux in the core of the transformer and thus special design considerations must be made to accomodate it.
However, in point of fact this is a quite-rare fault. It can be covered with a GFI instead of a shield, if you wish to.
Electrolysis, which is the subject of this thread, is not prevented by unbonding the boat from shore power in any scenerio and attempting to make an "electrical island" out of your boat when docked at a marina is doomed to fail in some way.
Yes it is UNLESS the electrolysis is caused by a fault ON YOUR OWN BOAT.
If the fault is on your boat then isolating the grounds will do nothing.
However, if the fault is on a NEIGHBORS boat then it will stop YOUR (but not his) damage. If he is leaking current down the ground conductor on HIS boat then your "ground" will be at some potential ABOVE ground. That voltage is then present on ALL the ground wires in the marina. The closer you are to the fault, the more of the current your boat sinks. As it sinks that current back to the actual ground your zincs erode at an accelerated rate.
Using an isolation transformer to protect against stray currents can work as well as protecting against transients, but it has nothing to do with the bonding of the neutral or lack thereof.
Ted
You don't bond neutral, you BOLT neutral.
Neutral (grounded conductor) and ground (safety ground) MUST BE BOLTED at one and only one place - it is to be done
at an energy source.
Therefore, your Genset must have neutral and ground bolted together
at the genset and when running on generator your boat
MUST NOT connect ship's ground to shore ground. This is why your genset breaker or rotary switch on the AC panel has THREE poles and not TWO. Your isolation transformer, if it is operating as an isolation transformer, has NO ground connection to shore; it is an energy source and thus neutral and ground are BOLTED at the transformer secondary.
If you are running on shroe power and have NO isolation transformer than you MUST NOT connect neutral and ground together on board the boat ANYWHERE. Doing so is a very serious error and raises both shock risks as well as CREATING electrolysis not only in your boat but also in those around you at the marina, because there typically is a 2-3V (not millivolt, VOLT!) offset between the grounded conductor (neutral) and safety ground, depending on the amount of load present on that wire.
If you bolt neutral and ground when they should not be, you will cause that ground offset to appear on ALL of your underwater metals!