I have a 14 year old Cruisair FX16c condensing unit that is shutting down intermittently with a high pressure fault. I have monitored the high side pressure with gauges and confirmed normal operating pressures during these events. My assumption is that the high side sensor needs to be replaced.
Can that sensor be swapped with the system charged (is there a check valve) or does the R22 have to be recovered before the swap out because it will open the high side line to the atmosphere?
Thanks,
George