Bill Allen
Well-known member
- Joined
- May 24, 2005
- Messages
- 819
- Hatteras Model
- 43' DOUBLE CABIN (1970 - 1984)
Robin thought I should post this, i've been having a shut down problem with my genset. It would run for twenty minutes (about) then shut down. Restart it and run for maybe five minutes. Checked all the shutdowns, changed filters, trouble shut everything we could. Never had to reset the shut down button. Talked to my generator guy since I didn't have to reset he sugested it was either the shut down reset or the fuel shut off solonoid. Replace the reset in the keys thought it was fixxed. Left the keys and it started it's games again. Had the solonoid on hand so changed it, no diference. Called my generator guy once again he was stumped but said he would call another buddy of his in the business and pick his brain. He called back said his buddy had a situation where the 30 amp fuse holder between the starter and control circut had gotten hot and took the spring tension out of the fuse holder and although it wasn't doing quite the same thing as mine he sugested changing it out. My first thought was bullshit, but nothing else seemed to be wrong with the unit so I changed it out, really didn't look bad to me. Started the geset up and that was it, i'm still amazed, but it is an Onan. Ever get up in North Jersey and need a very good generator guy Call Heman and his sons at Ocean Power. Bill