I have a 2002 16k btu Cruisair remote dx unit that has the following problem. The charge levels are running well below the chart guidlines at 48 psi suction and 175-200 psi liquid. The evaporator delta t is 18-23 degrees. The filters are clean and the airflow seems reasonable. The unit cools well starting at high load and superheat is running high at 30-40 degrees but as soon as you hit a normal evap load (78 degrees and less than 50% humidity), the superheat crashes towards zero and the suction line starts freezing at the suction service valve. The low suction pressure and initial high SH suggest a low charge but thefinal cooling stage at low load act like an overcharged system or a system with low evap airflow. Where do i go from here? Thanks,
George
George