After turning all off and removing all power from the boat, including inverters off,, turn the rotating knobs stright up/down.
The rotating knobs have screws in the center. Loosen these screws two turns max and slide whole knob off of the shaft. Remove the #10 screws from around the panel edges and swing open on the hinge.
You just want a peek or after a repair?
I'm still struggling with inverter project. Was going to supply inbound ac to the quattros through the #2 service panel.
Sensing the power in the #2 panel would then trigger two cases.
Case 1: Panel #2 hot - coil relay switch opens the inverter ac out to panels #1 & 2, all fed through the 70a breakers.
Case 2: Leaving the dock - #2 70a breaker open, ac in to quattros off, relay closes inverter out switches to Service Panels 1&3, Panel #2 cold, coil relay closes the ac switches allowing inverter ac out to service panels 1 & 3. #2 70a breakers is open, so no backfeed through the selector switch.
This works when #2 Service Panel 70a 3 pole is open at the panel. But if power is lost without opening this breaker in advance, such as when an unplanned loss of dock or Genetator ac power, the inverter will backfeed through the selector switch causing havoc - no bueno.
I was thinking if I could power the quattros before the 70a breakers then the #2 70a being open wouldn't matter.
All very challenging to me, but have no one up here who will help. So trying to figure it out.
If this doesn't make sense (shocking) I could post my text schematic.
On the positive side, I understand the electric system much better now, just not enough to not do something stupid.