Trying to get to the backside of the main distribution panel. Left side has continuous hinge. The panel has many small crews around the perimeter.

Do the screws have to come out or is their a frame which swings on that hinge?
 

Attachments

  • 20260821_101058.webp
    20260821_101058.webp
    193.7 KB · Views: 20
After turning all off and removing all power from the boat, including inverters off,, turn the rotating knobs stright up/down.
The rotating knobs have screws in the center. Loosen these screws two turns max and slide whole knob off of the shaft. Remove the #10 screws from around the panel edges and swing open on the hinge.

You just want a peek or after a repair?
 
After turning all off and removing all power from the boat, including inverters off,, turn the rotating knobs stright up/down.
The rotating knobs have screws in the center. Loosen these screws two turns max and slide whole knob off of the shaft. Remove the #10 screws from around the panel edges and swing open on the hinge.

You just want a peek or after a repair?
I'm still struggling with inverter project. Was going to supply inbound ac to the quattros through the #2 service panel.

Sensing the power in the #2 panel would then trigger two cases.
Case 1: Panel #2 hot - coil relay switch opens the inverter ac out to panels #1 & 2, all fed through the 70a breakers.

Case 2: Leaving the dock - #2 70a breaker open, ac in to quattros off, relay closes inverter out switches to Service Panels 1&3, Panel #2 cold, coil relay closes the ac switches allowing inverter ac out to service panels 1 & 3. #2 70a breakers is open, so no backfeed through the selector switch.
This works when #2 Service Panel 70a 3 pole is open at the panel. But if power is lost without opening this breaker in advance, such as when an unplanned loss of dock or Genetator ac power, the inverter will backfeed through the selector switch causing havoc - no bueno.

I was thinking if I could power the quattros before the 70a breakers then the #2 70a being open wouldn't matter.

All very challenging to me, but have no one up here who will help. So trying to figure it out.
If this doesn't make sense (shocking) I could post my text schematic.
On the positive side, I understand the electric system much better now, just not enough to not do something stupid.
 
I'm still struggling with inverter project. Was going to supply inbound ac to the quattros through the #2 service panel.

Sensing the power in the #2 panel would then trigger two cases.
Case 1: Panel #2 hot - coil relay switch opens the inverter ac out to panels #1 & 2, all fed through the 70a breakers.

Case 2: Leaving the dock - #2 70a breaker open, ac in to quattros off, relay closes inverter out switches to Service Panels 1&3, Panel #2 cold, coil relay closes the ac switches allowing inverter ac out to service panels 1 & 3. #2 70a breakers is open, so no backfeed through the selector switch.
This works when #2 Service Panel 70a 3 pole is open at the panel. But if power is lost without opening this breaker in advance, such as when an unplanned loss of dock or Genetator ac power, the inverter will backfeed through the selector switch causing havoc - no bueno.

I was thinking if I could power the quattros before the 70a breakers then the #2 70a being open wouldn't matter.

All very challenging to me, but have no one up here who will help. So trying to figure it out.
If this doesn't make sense (shocking) I could post my text schematic.
On the positive side, I understand the electric system much better now, just not enough to not do something stupid.
Don't be in a hurry. I have some sketches and notes from a big Hatt inverter install plan.
On a road trip now, back tonight.

Question, are the devices you want on inverter, in one breaker panel?
Ie: fridge, freezer, icemaker, lights and outlets?
 
I have 2 - 5000w quattro inverters and wanted to run the #1 panel (galley) and the #3 panel (house loads sans the water heater, dryer, and 32v charger) in a split phase configuration. The #2 panel has mostly a/c units which can't reasonably be powered of a lithium battery bank so was excluding it.
I appreciate your help Ralph.
 
P.S. I would not run oven of SP #1 while inverting.
 
It sounds like you bought the Victron equipment. You should go directly to the distributor, they go through extensive training in order to be able to sell that equipment. I purchased mine from Scott and he helped me every step of the way and is still helping the new owner of our boat.
 
Scott was not comfortable with the EG4 LiFePo4 server rack batteries my kids had purchased for the project and declined to work on the project.
In all fairness to him, it was two years ago and perhaps things in the industry have changed. The project has been a start / stop thing due to health issues, so I have just picked it up again.
I have no issues with Scott, he has helped me on numerous occasions and in fact I have purchased 3 Raritan Elegance toilets from him last year.
I'm just trying to finally push this project forward with the resources I have.
You are correct on the Victron equipment being the best. On Scott's advice I returned all the other stuff to the vendor and they swapped it out for Victron; all except the batteries which they had just gotten approval from victron to integrate through a communications translator which connects to the Gerbo allowing it to see and set the parameters on each batteries BMS. In fact, they became Victron dealers.
I encourage all here to include Scott in your projects, he is very knowledgeable and experienced.
It just didn't work out on this one.
 
The issue seems to be where to tap into the ac system where it won't backfeed the inverters. Anybody know where?
 
Its not a simple thing to do properly.
The first problem is that no two boats are alike. Small changes can be a problem.
Most installs I've seen from DIY customers and half assed electrical contractors are a mess. Usually having poorly terminated wires and dangerous logic or incorrect design.
Its not marine but shows how not to do things.
 
Thanks Scott for the post. Will objected to 6 practices:
1. I have 6-48v (UL Listed w/ a BMS and communication) which will be wired in parallel, not series to a bus bar, not cables.
2. The bus bars are solid copper, tinned installed on either side of the batteries connected with 8" 6awg tinned and lugged cables.
3. All cables are Ancor solid copper tinned with Ancor copper/tinned lugs, not soldered but cold welded with a power hydraulic crimper and finished with shrink tube.
4. From bus bar to a T-Class 300a fuse then to blue sea disconnect switch with 4/000 cable.
5. 4/000 continues into Victron Lynx Distributor through two Mega fuses into two separate quatteo feeds on 2/000 cable including grounds.
6. Victron Gerbo to control the battery side.
--------
The task before me is to incorporate the Quattros into main system. Hopefully in a split phase configuration but that is where the train falls of the rails. The marine world is unique, everything even within the brand, is custom.
So I think the install up to now passes muster, I just need help to facillitate a quality integration into the boat.
Scott, since most of the gear is already purchased, perhaps you might consider a consulting gig to talk me through the balance of the project.
 
6 awg is not sufficient for a battery. A t class fuse need to be at each battery with an individual switch.

My systems have each batter on a fuse then a switch then 4/0 cable to the buss bar. A fuse and switch between the buss and each inverter.

Id not consider any wire smaller than 2/0
 
I could not find any Hatt breaker pictures in my computer. So I will try to explain what my thoughts were.

Unlike a home styled breaker box where the breaker plugs into a power slot, tension holds the breaker in place and the load wire is attached with a lug screw, The Hatt AirPax breakers are screw mounted in the box. Power in is attached to the breaker with a lug screw/nut, load wire out is attached with another lug screw.

Power from those big panel switches and big panel breakers, connected to the load breakers with some nice big cables.
From these big power cables, a matrix of jumper cables are used to supply 115 or 230Vac to the single or dual breaker sets. Hatteras even used a puzzle of metal plates eliminating some of these jumper cables and crimps and some issues with them.

My thoughts were to interrupt this power in matrix with a second power source,, from an inverter.
This way, your just running a couple of extra power cables into the breaker/load boxes.
All of the loads, breakers and their wiring remains un-touched.

Your heavy loads stay connected to the shore or gen-set power, Your lighter loads, Fridge, Lights and Outlets are now on inverter.

Somewhere else you mount your inverter, another breaker panel and an inverter by-pass switch.

My comments above are just to help explain that a simple job can stay simple, not how to do it.
PLEASE READ MY NEXT COMMENT CAREFULLY;

THIS IS NOT your Radio Shack home crystal radio set. These same wires can kill you and others AND burn your boat out of the water.
Even if there is no smoke, your insurance company could have a cow if a proper marine tech was not a part of these mods.
 
I'm still struggling with inverter project.
All very challenging to me, but have no one up here who will help. So trying to figure it out.
If this doesn't make sense (shocking) I could post my text schematic.
On the positive side, I understand the electric system much better now, just not enough to not do something stupid.
Please find a tech. Take your boat to a town where the guy is or bus/fly him in.
 
Thanks Ralph. I appreciate you putting our safety before a bunch of bravado for the benefit of the forum.
I have found a couple abyc guys in Florida and South Carolina, also victron dealer at Kentucky lake who said they would do it. I just wanted to put this behind me and move on to the other overly ambitious projects.
I did offer to fly a certain expert we all know and love, however, no joy. Of course that was a couple of years ago.
I do have a working Outback 3500, but was attempting to yank the house loads off the port starter bank.
Maybe if I doubled up the port starter bank that would provide some additional headroom.
Who knows, maybe the expert will have a change of heart...
Regards
 
I have some schematics for a split phase Quattro 5000 for a 56MY. I drew them a couple of years ago. I can post them sometime when I have access to the files.
 
Great. That would be most helpful.
 
IMG_5346.webpIMG_5347.webp
Not sure if it was done correctly or not (and I’ve since restored it to how it left the factory) but a previous owner fed their inverter into this panel at the bottom left “special use” breaker which fed 2, 4, 7, 9 & 11. When I bought the boat there was no inverter on board and the wire leaving breaker 6 went to a terminal block and came right back and fed the buss bar for 7, 9 & 11.
So now the out and back 3 wire is removed and the jumper is back and the cover re-labeled. And looking at I now, I see why they had the charger set to 120v using only breaker #3 (Ive since changed it to 240).
 
Hatteras even used a puzzle of metal plates eliminating some of these jumper cables and crimps and some issues with them.
Yep, you have the better installation design with the puzzle plates feeding your breakers.

My idea was to separate (cut the plate jumpers) with power from the inverter. Then, just let the ship power the heavy loads.
No accidental over load on the inverter, inverter would act like a UPS and keep all running during power failures, switching from shore to gen-set or all still for those quiet evenings when gen-sets are not required.
All digital clocks stay on also.
 
Yep, you have the better installation design with the puzzle plates feeding your breakers.

My idea was to separate (cut the plate jumpers) with power from the inverter. Then, just let the ship power the heavy loads.
No accidental over load on the inverter, inverter would act like a UPS and keep all running during power failures, switching from shore to gen-set or all still for those quiet evenings when gen-sets are not required.
All digital clocks stay on also.
IMG_5457.webp
Oh, they cut plates too🤣. That was how they decided to feed a bunch of 12V updated stuff (heads, shower sumps). They did it without a fuse coming off the gen start battery and without a main breaker in the panel. I’ve since added both.
 