Today, out of nowhere, one of my 240VAC HVAC systems started tripping the GFI every time I turn it on. Trips, even if I just turn to "START" without running the compressor.
All of my (four) HVAC systems a connected to this same breaker/GFI in the pilothouse (58LRC). Only the salon HVAC trips the breaker, so this is a bit strange.
If I start the generator and run off Generator power, the breaker does not trip. So, something to do with shore power and this one HVAC system.
I'm thinking it must have something to do with the 220VAC water pump circuit as that will trip the breaker when the Salon HVAC is turned on without the compressor.
We have had a lot of rain lately. Maybe water got in somewhere? I opened the HVAC control box and it's dry. There was one white wire connected to a capacitor that was melted. It was corroded badly at the spade connector, so I cut it off and replaced it with a nice clean connection. I thought that might have been the culprit, but no such luck.
Any ideas?
Welcome to the Hatteras Owners Forum & Gallery. Sign Up or Login
+ Reply to Thread
Results 1 to 6 of 6
Thread: Strange issue, tripping 240V GFI
-
Strange issue, tripping 240V GFI
-
Re: Strange issue, tripping 240V GFI
Disconnect all wires from that same cap and re-test.
It is amazing how many A/C caps fail and cause strange problems.
-
Re: Strange issue, tripping 240V GFI
Good plan, will try in the morning.
-
-
Re: Strange issue, tripping 240V GFI
Well, the Gremlin that was in my HVAC must have gone home. All is working perfectly again and nothing (that I know of) has changed. Went down to the boat, turned the unit on and it ran for two hours, no issue.
Bizzare.
-
07-13-2021 02:11 PM #6
Re: Strange issue, tripping 240V GFI
Intermittent issues are a PITA.