    ONAN 20 kw Over rev shutdown

    Oh no, it's an ONAN.

    During last weekends trip, I gave the generator a good workout. Ovens, AC, hot water heater, chargers, all the usual stuff.
    After about 8 running hours funny things began to occur. First, the forward AC began making a clicking sound like a auto turn signal. Then the fridge light began flashing while the trash compactor was operating. Then there was a sound of the generator reving up followed by an immediate shut down.

    I let it cool for about 2 hours, with all loads off, pushed the fault reset button and it started up. Turned on just the MSTR AC (it was still hot in Miami last week) and it ran great all night. Next day I restored normal loading except hot water heater and still ran great for a few hours. Early evening it began acting up and heard the over rev followed by auto shut down.. Restarted it and ran ok for a few hours. Curious, I began shedding load and heard the genny begin to over rev again.


    OK, what I suspect is happening is whatever regulates the engine speed to the demand is going funky. I think as devices switch on an off, the gen motor is not reacting to the reduced load and going into over speed fault shut down.

    So, I'm looking for suggestions on how to diagnose and fix. Any ideas?

  2. #2

    Re: ONAN 20 kw Over rev shutdown

    It could be the Governor not adjusting. See if you can reproduce the fault while monitoring frequency. RPM directly affects frequency not voltage

    I would avoid using any sensitive electronic controlled aplliances and compressors. Try with the water heater, a non Induction cooktop, non digital oven, electric grill etc.

    If you need a pro there is a really good Onan specialist here in Miami, he s American so he won’t have any issue venturing north of the border aka Miami Dade county line
    Pascal
    Miami, FL
    1970 53 MY #325 Cummins 6CTAs
    2014 26' gaff rigged sloop
    2007 Sandbarhopper 13
    12' Westphal Cat boat

  3. #3

    Re: ONAN 20 kw Over rev shutdown

    Sounds like a faulty governor to me.

    Pic of the injection pump would help so we can see what it is and what kind of governor it has.
    --- The poster formerly known as Scrod ---

    I want to live in Theory, everything works there.

    1970 36C375

  4. #4

    Re: ONAN 20 kw Over rev shutdown

    Quote Originally Posted by Avenger View Post
    Sounds like a faulty governor to me.

    Pic of the injection pump would help so we can see what it is and what kind of governor it has.
    Not good a posting pictures but it's a Stanadyne DB2-4086 rpm is 1800

  5. #5

    Re: ONAN 20 kw Over rev shutdown

    The governor on the oh no is electronic, mdl4. There is an over rev sensor. To me, what you discribe is a generator running close to one of it's shut down parameters. Check the simple things first... like the impeller, and obstruction in the strainer.. if it's running hot, the thermal exhaust or coolant temp could shut it down, but mine acts up before the auto shutdown trips. Your auto shutdown tripped, so I'm guessing it's your impeller or exhaust temp sensor. Replaced both of mine in the last few weeks, easy fixes. Onan will tell you the exhaust temp sensor is unavailable, but there is a substitute.
    Last edited by dottieshusband; 11-14-2019 at 05:13 PM.

  6. #6

    Re: ONAN 20 kw Over rev shutdown

    Quote Originally Posted by dottieshusband View Post
    The governor on the oh no is electronic, mdl4.
    The pump spec shows up as mechanical. Would they have been retrofitted? Seems an expensive proposition for a generator in a Viking.
    --- The poster formerly known as Scrod ---

    I want to live in Theory, everything works there.

    1970 36C375

  7. #7

    Re: ONAN 20 kw Over rev shutdown

    Quote Originally Posted by dottieshusband View Post
    The governor on the oh no is electronic, mdl4. There is an over rev sensor. To me, what you discribe is a generator running close to one of it's shut down parameters. Check the simple things first... like the impeller, and obstruction in the strainer.. if it's running hot, the thermal exhaust or coolant temp could shut it down, but mine acts up before the auto shutdown trips. Your auto shutdown tripped, so I'm guessing it's your impeller or exhaust temp sensor. Replaced both of mine in the last few weeks, easy fixes. Onan will tell you the exhaust temp sensor is unavailable, but there is a substitute.
    The voltage regulator is electronic but the Governor, on the engine by the injection pump, is mechanical and regulates RPM to 1800 Two different things

    If the engine is reving up it s not an overheating Or water flow issue. And if there was an overheating issue, it would happen under load, not reducing loads. There would also be tell tale signs like sound and steam.
    Pascal
    Miami, FL
    1970 53 MY #325 Cummins 6CTAs
    2014 26' gaff rigged sloop
    2007 Sandbarhopper 13
    12' Westphal Cat boat

  8. #8

    Re: ONAN 20 kw Over rev shutdown

    like everyone else has said it sounds like a governor issue . The AVR senses voltage and adjusts the excitation voltage (in DC) to keep the AC voltage in the proper parameter, lower DC excitation voltage lower AC output. The governor keeps the engine running at 1800 rpm regardless of load. That determines your frequency. When all is right the no load frequency should be 62-63 HZ. Fully loaded it's ok to be 59 or so. The ac out voltage should be 240 volt or close to it. (there is an adjustable pot to adjust the AC voltage on the AVR. This all assumes it is a 240 v unit which is what Hatteras used in most cases. I hope this helps! I have learned a whole lotta OH- NO control stuff this past year . I believe the AVR also can induce a shutdown if the governor does not keep the operating RPM - 1800. IRRC it would take out the CB2 breaker at that point ....Pat
    Last edited by doc g; 11-14-2019 at 07:16 PM.

  9. #9

    Re: ONAN 20 kw Over rev shutdown

    Yes, when things were going funky this weekend, output voltage was 240v.

  10. #10

    Re: ONAN 20 kw Over rev shutdown

    If you'll Google radionerds images stanadyne, it will bring up the manual for the db2 pump on the mdl4. The governor isindeed internal to the pump. Although I had the exact symptoms a few months ago, irregular running, irregular rpm's voltage variation, shutting down etc... pumping water just fine. Initially replaced the exhaust temp sensor, which fixed it for a while, but ultimately it turned out to be a deteriorating impeller, and blades obstructing flow to the heat exchanger.. Hey, by all means, pull the injector pump first..