  1. #1

    New Generator (s)

    After much deliberation, I've decided to retire my 20kw Onan MDL4. This is a forced retirement as the unit still works just fine. It has had a small oil leak since I bought the boat. Not much, just a few drops a day, maybe a cup a month. I decided to finally figure out where it was coming from and it turned out to be the fitting on the oil pan drain plug for the oil exchanger... looks like an easy fix.. BUT.. the PO or his hire has slathered the fitting with some kind of silicone goop... and based on other "repairs" I've seen on the boat... I gots me a real bad feeling.. and I'm not going to worry about it... so it's outta here.. going back with 2 generators... a 16EKOZD Kohler, and 9EKOZD Kohler for a quieter nighttime unit. I'll post pictures as we progress, and once the old unit is on the dock, it'll be available with spares.

  2. #2

    Re: New Generator (s)

    How many hours Did you get out of the old genny?

  3. #3

    Re: New Generator (s)

    Quote Originally Posted by Passages View Post
    How many hours Did you get out of the old genny?
    Hard to say.. it's about 1200 since rebuild, but I don't know what it had on it at rebuild time. It still runs just fine, makes good power, no smoke or oil consumption.. other than the leak.. but even in the sound shield, it's loud.. I'll look at the Hobbs in the morning.

  4. #4

    Re: New Generator (s)

    Wise choice on the big and small sets. Interested to see how it all goes and how you like the results. Didn't Bruce used to sell Kohler gensets? I think so. Post photos if you can.

  5. #5

    Re: New Generator (s)

    I'm also 'retiring' my ONAN. After doing the load calculations, I'm looking at fitting soft-start to the aircon compressors and then one of three options -

    1) One gen 50% smaller than the 20kw original or,

    2) a 5kw gen for most 'AC stuff' most of the time and a 7kw gen mainly for the aircon with some backup for 'AC stuff' or,

    3) a 5kw battery/inverter combo and 7kw gen for just the aircon.

    I prefer the simplicity of 1, the flexibility of 2, the technology of 3. Will probably go like you with the 2 gen option and leverage the soft-start to keep the size/cost down

  6. #6

    Re: New Generator (s)

    Quote Originally Posted by Skytinerant View Post
    I'm also 'retiring' my ONAN. After doing the load calculations, I'm looking at fitting soft-start to the aircon compressors and then one of three options -

    .......Will probably go like you with the 2 gen option and leverage the soft-start to keep the size/cost down
    The softstar is the REAL DEAL. See my thread here (especially post #8) https://www.samsmarine.com/forums/sh...-to-run-my-A-C

    I would get the smallest possible generator. And use soft starts. Also, you can get a small generator and get a "hybrid" inverter that will boost the generator when higher loads come on (starting AC, old lady runs hair dryer, etc). I'd seriously consider the hybrid inverter and just 1 small/quiet generator, especially if you don't mind a tiny bit of load management (don't use range, hot water heater, and all A/C at once).

    EDIT: Also read post #35 where the Harbor Freight out performs the Honda: https://www.samsmarine.com/forums/sh...907#post321907
    FTFD... i drive a slow 1968 41c381