Re: 3 Position Rotary Switch p/n etc?
Semper Siesta
Robert Clarkson
ASLAN, 1983 55C #343
Charleston, SC
-
02-20-2018 06:40 PM #12
Re: 3 Position Rotary Switch p/n etc?
Right. That is not the case. Sorry I wasn't clear. The path looks like this:
Hubbel "Source" connector -> two 50 Amp slow burn fuses -> Interior Distributon Panel -> 50Amp (220v) Breaker -> Rotary switch -> triple load panels -> Triple 70amp Breaker (with neutral as well) -> Sub Panels in Engine room and under pilot house (no input breaker IIRC)
-
Re: 3 Position Rotary Switch p/n etc?
Each source has its own isolation transformer. Get out your wiring schematics and look at what is on there. You should also have breakers on Source 2 for the 120v 50a inlet that is under the two 240v inlets on each side of the boat. Those breakers are somewhere. Mine are in the stbd engine room. I'm not sure where they are located on a 61.
You may want to pull the cover on the transformers and check the input and output voltages there (primary and secondary).
Test across terminals X1 and X2 and compare to voltage across H1 and H2.Last edited by SKYCHENEY; 02-20-2018 at 10:02 PM.
Sky Cheney
1985 53EDMY, Hull #CN759, "Rebecca"
ELYC on White Lake--Montague, MI
-
02-26-2018 02:41 PM #14
Re: 3 Position Rotary Switch p/n etc?
Well all said and done it was the breaker in the generator compartment isolator panel where there are two 50amp breakers that were popped. I am very relieved that it wasn't rotary switch!
-
Re: 3 Position Rotary Switch p/n etc?
Semper Siesta
Robert Clarkson
ASLAN, 1983 55C #343
Charleston, SC
-
02-26-2018 05:10 PM #16
Re: 3 Position Rotary Switch p/n etc?
I hear you. I would expect the slow burn fuses to go first. On source 1 they did. It seems that on our boat source 1 may not be on the isolation transformer!? On the other hand I had a ton of load. 4 A/C units and 3 space heaters and was not paying attention. I also am reasonably sure that I have a bad compressor on the master A/C which was pulling ridiculous amounts of load on ships service 3. It was avoidable.
Where did you source the breakers from? I may get a spare or two!
-
Re: 3 Position Rotary Switch p/n etc?
You'll need to get the numbers off what you've got. No one had mine, but I found one on E-bay.
Semper Siesta
Robert Clarkson
ASLAN, 1983 55C #343
Charleston, SC
-
02-26-2018 05:50 PM #18
Re: 3 Position Rotary Switch p/n etc?
Do you know if they are common with the other 50 amp panels?
Check this out:
http://www.airpax.net/pdfs/209.pdf
My main panel had a P/N of "50-50-2-63-1" which is how I found it.
20180219_234643119_iOS.jpg
-
Re: 3 Position Rotary Switch p/n etc?
Don’t forget to ask Sams. If they don’t have them they can help direct you. You’re lucky.